几何尺寸与公差论坛

 找回密码
 注册
查看: 469|回复: 0

aci 318 chapter 20

[复制链接]
发表于 2009-9-7 09:43:30 | 显示全部楼层 |阅读模式
aci 318 chapter 20
i've got another post going on鈥?
well, i'll post my experience here - but others out there - do add any insights above and beyond this:
i did a load test once on a small grandstand - made of load bearing cmu with double tees forming each riser.  no one had a clue where the dt's came from and what load capacity they truly had.
i had a number of barrels set up in a specified spacing to load the grandstand to 125% of the required live loading for grandstands (100 psf i think it was).  the loading was performed by adding water to the barrels - calculating the volume in each barrel, the resulting weight, and the barrel spacing to mimic 100 psf.
i took vertical elevation measurements of the dt's prior to loading, at 1/4 loading, 1/2, 3/4 and full loading.  then removed the load, took measurements, and then took them again i think at 24 hours later.  (i don't have aci with me right now but this is what i recall).
aci provided design criteria for the deflection and deflection-rebound.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2024-7-1 11:09 , Processed in 0.033323 second(s), 19 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表