几何尺寸与公差论坛

 找回密码
 注册
查看: 632|回复: 0

asce 7-05 out-of-plane seismic forces

[复制链接]
发表于 2009-9-7 13:09:13 | 显示全部楼层 |阅读模式
asce 7-05 out-of-plane seismic forces
in asce 7-05 section 12.11.1, the out-of-plane forces for structural walls (shear and/or bearing) are 0.4sdsiwp with a minimum of 0.1wp.
these forces are also used for anchoring or bracing the top and bottom of the the wall sections. a minimum anchorage load is given in section 12.11.2.
if a flexible diphragm is used for a c, d or e category building, the anchorage force doubles to 0.8sdsiwp (section 12.11.2.1). the code does not specifically state that the wall should be designed for out-of-plane forces (bending and shear) to this magnitude, only the anchorage.
is this how you read it? do you design the wall reinforcing and thickness for 0.4sdsiwp for all situations unless wind controls?
find a job or post a job opening
i read it the same way, the anchorage is designed for the greater force but not the wall. note also the steel anchorage increase required in 12.11.2.2.2.
"do you design the wall reinforcing and thickness for 0.4sdsiwp for all situations unless wind controls?"
yes
thanks haynewp.
as for out-of-plane wind loads, i use the components & cladding wind load.  when the wind blows in this direction, this wall can't normally contribute any shear resistance as a part of the mwfrs.  to calculate the effective area for c&c, i use the height h between the support levels to get the area = h*h/3. is this what everyone else does?
if i re  
i got h*h/3 from the definitions in 6.2. the other option would be to multiply the height by a strip width of 1 foot, 16" or perhaps the the rebar/grout spacing.
effective wind area, a: the area used to determine gcp. for component and cladding elements, the effective wind area in figs. 6-11 through 6-17 and fig. 6-19 is the span length multiplied by an effective width that need not be less than one third the span length.
right, "need not be less than one third the span length".
basing it on a 1 ft strip x h would be quite conservative. i could also see an argument made for the width being based on the reinforcing spacing.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2025-1-11 05:36 , Processed in 0.039402 second(s), 19 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表