i'm working with the canadian building code...which i left iin the office.  can someone give me the load combination factors for limit state design for d+l ans d+l+siesmic....thanks in advance....i believe the section is 4.3.1
check out our whitepaper library.
from ontario building code 4.1.3.2
1.25d + 1.5l
if d resists overturning, uplift or reversal load effect,
0.85d + 1.5l
seismic:
1.0d+gamma1.0e
plus
1.0d + gamma(1.0l+1.0e) storage and assembly occupancies
or
1.0d + gamma(0.5l + 1.0e) for all other occupancies
gamma = importance factor, = 1.0 "for all buildings, except for those where it can be shown that collapse is not likely to cause injury or other serious consequences, it shall be not less than 0.8"