checker plate floor loading
existing 1/4" thick steel checker plate floor is under scrutiny.  i'm having difficulty finding a method to determine the maximum allowable concentrated load.  a typical plate is rectangular and simply supported on four sides, is removable so not fastened to supports.  the load is gravitational so is perpendicular to the plane of the plate.  the plates vary in size but an example would be 3 feet by 4 feet.  any thoughts?
to truly calculate it, you could do a fea.
personally, i'd use the "floor plate bending capacity" tables in the steel manual, and calculate the equivalent point load from the moment the uniform load would create.
page 2-145 in the 9th ed.
pages 3-154 & 155 in the 13th ed.
hope it helps
i agree with chipb... also, in table 3-18a, you have the moment of intertia per one inch strip. you can calculate your maximum allowable deflection... i'm sure "what it looks like" is more of a concern than the actual yielding anyway.
roark's formulas for stress and strain. 6th ed. table 26 case 1b.
a=4 b =3.  b/a = 1.33   beta = 0.74  alpha = 0.0093
max def = alpha x w x b x b / ( e x t x t x t)
max stress = (3w /(2 x pi x t x t)) x ((1 + poison ratio) x
ln(2b/pi x r'o) + beta))
r'o = sqrt (1.6 ro x ro + t x t).
ro = radius of load contact
bagman
my 5th edition table 25 shows:
alpha=.1478 at a/b=1.2
alpha=.1621 at a/b=1.4
i think to get roark's formula to work, you'll need dimensions in inches (to match psi).
my calcs show that the method of finding an equivalent concentrated load from the distributed load tables in the steel manual is very conservative in comparison to the result given by roark's formula from table 26 case 1b.  the resulting max point load per roark is about twice that of the first method.  the plate's support on four edges apparently makes the difference.  the first method assumes support on only two edges.  thank you all for your help!
side note:  table 3-18a in steel manual gives moment of inertia per one foot of width, not one inch - a minor correction to the contribution by brane23.
asce 7-05, 4.3- concentrated load is over a 2.5' square area.
i have asce 7-02 which reads "unless otherwise specified, the indicated concentration shall be assumed to be uniformly distributed over an area 2.5 ft square and shall be located so as to produce the maximum load effects in the structural   
the alpha figures i posted earlier were, in fact, for table 26, case 1b.  interpolating, i get alpha=.158, which gives 0.46" deflection under a 1 kip load.
您需要登录后才可以回帖 登录 | 注册