design of water retaining structures to bs8007
i am currently designing a water retaining structure in dubai to bs8007
appendix a of the code gives values of t1 for concreting in the uk but gives no guidance on the value of t2 (temperature fall because of seasonal variations)
as the climate in dubai is much hotter than the uk what values of t1 and t2 should i assume for the design?
to 240850
check publication "guide to the construction of reinforced concrete in the arabian peninsular," published in 2002, joint publication of 'the concrete society' & 'ciria.'  this was originally published as a ciria special publication 31 in 1984.
* ciria, 6 storey's gate, westminster, london sw1p 3au, uk.
* tel +44(0)20 7222 8891
* fax +44(0)20 7222 1708
to 240850
i forgot to mention, dubai is included in the ciria publication.
regards
barry a