floor live load reduction ubc 97

[复制链接]
发表于 2009-9-9 12:47:06 | 显示全部楼层 |阅读模式
floor live load reduction ubc 97
does anyone know if a dormitory / apartment second floor live load is alload a reduction?  according to the ibc 2000, a reduction is allowed.  i could of sworn that the ubc 97 allowed a 40 lb/sqft live load for the bedroom areas to be reduced to 30 lb/sqft.
check out our whitepaper library.
yes, there is a live laod reduction allowed in 1997 ubc.  it is the same as the one in the ibc.  you will not necesarily get a 25% reduction.  the reduction is based on the tributary area supported by the structural   
sperling - i believe it is:
%reduction = 0.08 (at - 150) <= 40%
thank you, i was going from memory.