how to specify self consolidating concrete
i've found a bit of literature about self consolidating concrete.  i'd like to use it on several exposed columns, but can't find any really helpful information about specifying it.  the closest i found was
if you haven't already, check with lafarge at lafargenorthamerica.com they are usually pretty helpful, and have scc they call agilia.
you could also try pci.org, or find a precast manufacturer in your area that has used it.  i re  
i am working in a project with extensive use of self compacting concrete. it is a very delicate product, good for our specific application, but i would not recommend its use unless you have to.
we specified
- slump (flow) wich will depend on your formwork and reinforcement configuration
- strength
- segregation (there is a segregation index)
- air content (as per normal concrete)
- temperature (as per normal concrete)
also contact the admix manufacturer.  i'm sure they'd be more than willing to help!
also contact the admix manufacturer(s).  i'm sure they'd be more than willing to help!