load sharing factor in timber design

[复制链接]
发表于 2009-9-10 11:11:37 | 显示全部楼层 |阅读模式
load sharing factor in timber design
i am carrying out an aashto timber dock design and want to make use of the load sharing factor (1.15).  please advise what the requirements are for making use of this factor.  i am working in the uk and unable to obtain a copy of aashto at present.  (i.e. i plan to space 6 no. stringers on 10 foot span - 21", i believe this is adequate but need confirmation and explanation).
find a job or post a job opening
see
bs 5268-2-2002 clause 2.10 states that a load sharing system exists when;
why are you using aashto criteria?  is the dock (or was that supposed to be deck?) design specified to be done according to aashto?  if not, use some other design code such as nds.