what is the long term deflection limitation for the two way concrete slab? aci 9.5.2.5(aci 318-99) eq 9-10 is too confusing, is any quick way to get the allowable deflection limitation to compare the result we got from ram concept?
happyday,
the code clause is pretty clear.
if you cannot understand it how are you going to understand how to manipulate ram concept to give reliable values for deflection, because the values it gives using the default settings will not be realistic allowing for cracking and long term effects.
see table 9.5(b) under "deflection to be considered"
ted
happyday,
your long-term amplification factor per aci 9.5.2.5 is (2) for accounting for creep and shrinkage in slabs. however, a multiplier of 2 is typically not adequate to estimate deflections in conventionally reinforced two-way slabs. several studies have indicated that a value of 3-4 should be used to estimate long term losses, or a lower modulus of rupture strength of 4*f'c^1/2 to account for cracking due to shrinkage restraint at columns. i would suggest the paper "long term multipliers for estimating two-way slab deflections" by graham and scanlon, aci journal nov-dec 1986. it has some good information that may help you determine the multiplier to use in concept. in addition, aci 435rfff"> control of deflections in concrete structures has information regarding the same topic.
good luck,
auce98
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2025-1-20 05:35 , Processed in 0.033566 second(s), 19 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表