几何尺寸与公差论坛

 找回密码
 注册
查看: 457|回复: 0

minimum reinforcing in concrete tanks

[复制链接]
发表于 2009-9-10 14:17:26 | 显示全部楼层 |阅读模式
minimum reinforcing in concrete tanks
in light of the recent discussion of minimum reinforciment of footings according to aci 318 (
i was of the belief that if you satisfy your flexural requirements, you then compare the total amount of steel to your temp/shrinkage minimum, for the whole section.  however, 10.5.4 of 350 seems to suggest that you should have the minimum temp/shrinkage on each face.  now, after re-reading 7.12.1 of 350, i see that it says, "the minimum reinforcement provided in any direction and on any face shall be the greater of shrinkage and temperature reinforcement or flexural reinforcement."  sounds like minimum shrinkage and temperature steel on each face.
but then, a little further on, 7.12.2.2 says the shrinkage and temperature reinforcement must be distributed so that no less than 1/3 of it is on any one face.  the accompanying commentary says that the s/t reinforcement is typically divided equally to each face.  this points back to my original argument, and also agrees with the pca book.
so, after all that, i have come full circle, back to my original position.  satisfy your flexural requirements, then compare the steel in the whole section to your minimum temp/shrinkage requirement.
i think most of the confusion of the engineers in the earlier post is due to failure to distinguish between flexural reinforcement and direct tension reinforcement.  flexural reinforcement is to provide strength, while direct tension reinforcement in things like floor slabs and tank walls is to limit crack widths.
it is perhaps unfortunate the way aci and other codes commingle the two, but engineers only need to keep in mind the distinction, and provide for both.  in walls where a strong degree of crack control is required, .0018 is certainly not enough.  so i expect your .005 is what is intended.  the australian code makes this .006, placed half each face for walls greater than 200mm thick.   
rholder98-
excellent point.  both of these articles are modified from aci 318, and, they seem to completely change the meaning.  i agree with your interpretation of article 10.5.4 of aci 350.
because you didn't mention formula (10-3), do you believe that 10.5.1 states that article 10.5.4 should be followed in lieu of formula (10-3) for a tank wall?  article 10.5.1 of aci 350 is identical to that of aci 318, and the upshot of the previous thread was that (10-3) didn't apply to slabs of uniforn thickness.  however, the examples in munshi's book check the provisions of 10.5.1, 10.5.3, and 10.5.4.
i think 10.5.1 does apply, because it says "at every section of a flexural   
hokie66-
i agree.  tank designers think a little differently from the rest.  that's why i started a new thread: to discuss this issue as it relates to tanks.
rholder98-
ok, so we seem to agree on all counts.  that is, i've been designing tanks the way you describe it.  
next, i've noticed that chapter 13 applys to "walls reinforced for flexure in more than one direction."  do you agree that a tank wall, though free at the top, qualifies as a two way slab?
one of the posts from the previous thread argued that two way slabs may have less stringent requirements than a one way slab.  article 13.3.1 makes no mention of article 10.5.1, but brings the designer directly to 7.12.  do you think that the minimums of article 10.5.1 are implied by the phrase "determined from moments at critical sections?"
i would follow both 10.5.1 and 10.5.4 aci 350. whichever is more stringent would govern.  aci 350 is quite clear in 10.5.4.  it seems a little much to use 0.005 on each face but aci is the law when adopted by the specs.  munshi is only an author. his book does not hold any weight with the building code. if you go to court if something goes wrong and say you used munshi instead of aci 350, your insurance will be the party paying.  i would use aci 350 10.5.4 & 7.12 literally until aci clarifies things.  it's a legal world sometimes, not only an engineering one.  i am now modifying an "old timers" design because he did not follow aci 350 exactly.  his design seems sound but the law is the law.
vincentpa, i disagree that 10.5.4 is "quite clear".  it says to use the minimum required by 7.12, but again, 7.12.2.2 says to distribute the temperature and shrinkage reinforcement to each face, so i don't think it's telling us to use the entire 0.005 on each face.
take a 12" wall, d=9".  10.5.1 says you need at least (200/60k)(12)(9)=0.36 in2/ft on each face.  i interpret 7.12 to say you need at least (.005)(144)=0.72 in2/ft total.  if you placed this on each face, you would double the required steel.  that does not make sense to me.
also, munshi is on the voting subcommittee of aci 350, so i would hope we could trust his interpretation of the intent.  i agree aci could use some clarification.
jmiec-
a tank wall, free at the top, does experience flexure in two directions, if the plan geometry agrees.  that is, a really long tank would behave more as a cantilever, until it reaches the corner.
i do believe 10.5.1, .3, and .4 are implied in 13.3.1.  here again, it refers to the minimum "in each direction" stated in 7.12, which i believe is total, not each face.
vincentpa-
i've come around to the thinking that tank walls are two way slab systems, covered by chapter 13.
article 13.3.1 simply states that "area of reinforcement in each direction for two way slab systems shall be determined from moments at critical sections, but not less than required by 7.12.
i read that to mean total reinforcement, not tensile reinforcement.
i agree that some authors misinterpret the code.  however, munshi's book is published by the portland cement association, so it carries a lot of weight with me.
rholder98-
i think article 13.3.1 implies the use of 10.5.1 and 10.5.3, but the wording of 13.3.1 overrides 10.5.4, since, chapter 13 specifically addresses tank walls (13.1.1), while chapter 10 seems geared towards one way slabs.