quick question. i have an existing building in canada (built in 1931), upon which the owners are considering putting up a monstrous air handling unit (length = 38ft, width = 13ft, height = 12ft, weight = 35,000 lbs). now i pretty much already know without calculating anything that it won't work, but my main question was about the snow loads surrounding the unit.
if i treat it as a rooftop obstruction, i get a snow drift of 75 psf max down to 33 psf, extending for a distance of 24 ft (twice the height of the unit). if i input it as a small upper roof with a step height of 12 ft, i get 75 psf down to 33 psf, over a distance of 11 ft +/-. would i need to consider the worst of the two conditions, or would i need to superimpose them together? seems to me i would only need to consider the worst of the two conditions, however a 24 ft long snow drift seems kind of ridiculous??
check out our whitepaper library.
users guide nbc 1995, structural commentaries (part 4), commentary h, snow loads, 39. 'areas adjacent to obstructions', (figure h6), should do it.
actually, fig. h-6 is what i used for the second case i ran up above. however, the plan area of the top of the unit is large enough to also generate built-up snow loads around the perimeter of the unit from the top of the mech unit. (based on fig. h-4(a) of nbcc commentary)
my ? was more about whether i would take the worst case of the two conditions or would somehow superimpose the results?
karlt...i would consider the worst case, though i agree your drift width of 24 feet seems a bit out of range. |
|