几何尺寸与公差论坛

 找回密码
 注册
查看: 440|回复: 0

seismic design, r coeff. question

[复制链接]
发表于 2009-9-15 20:47:45 | 显示全部楼层 |阅读模式
seismic design, r coeff. question
i'm designing a 15 ft high single story addition in sdc d, sug-ii, with log columns, glulam beams, and log "k-braces" for lateral force resistance.  the roof will be 3x6 t&g.  in asce 7-02, table 9.5.2.2 i'm trying to determine what r coefficient to use and i don't see any that look applicable.  they all seem to apply to steel, concrete, masonry, or wood shear panels.  does anyone have any experience with this?      
gib-
you are talking about a timber frame, in essence.  agree that the chart isn't much use for that particular lateral force resisting system.  there doesn't seem to be a lot out there about timber frame design.
however fyi some research results on timber frame lateral design at the following link:
scholar.lib.vt.edu/theses/available/etd-08142002-232925/
good resource for timber connection designs is timber framers guild,
ubc 1997 or cbc 2001, volume 2 has those r values based on your structural building components.  seismic design book by lindeburg and baradar-8th edition describe the procedures.  you may view this book at
fndn,
thanks.  it was there in the 1997 ubc, in table 16n.  r=5.6 for building frame system - heavy timber.  
is that r value ok to use if it isn't listed in the ibc?  just wondering if we can use r values that are not listed in the ibc, but are valid in other codes?
i don't see why not.  there isn't much of anything on log construction in the ibc, so you have to find resources elsewhere.  i have used the '97 ubc before when i ran into something that wasn't covered in the ibc.  as long as the item isn't prohibited by the ibc,  i would prefer to find another reference than try to make an educated guess.
gib2;
i should have added chapter 16 on my previous post. i am glad you found it.
thanks, gjb.  when the code isn't explicit on something, i use other references or codes for guidance.  just wondered what others thought about that.
according to ibc section 1614.1, exception #3, wood framed buildings constructed in accordance with section 2308, conventional light framed structures, do not have to be analyzed in accordance with section 1616.1, structural design criteria.
if your building can be considered conventionally light framed, and you abide by the detailing required in chapter 2308, you will not have to perform a seismic analysis.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2025-1-13 19:33 , Processed in 0.035374 second(s), 19 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表