几何尺寸与公差论坛

 找回密码
 注册
查看: 732|回复: 0

bolting bracket to concrete wall

[复制链接]
发表于 2009-9-7 16:15:49 | 显示全部楼层 |阅读模式
bolting bracket to concrete wall
hello
i have a bracket, 50" horizontal with a 24" vetical leg that i want to bolt to a concrete wall. the approximate load on this (spread evenly over the horizontal member)will be ~1000 pounds.
i plan to use (2) 3/4" bolts passing through the concrete and vertical leg.
my question... common sense would indicate the higher (closer to the horizontal)the better for the first hole. but.... what would be the minimum distance from this first hole to the second.
both bolts will share the shear forces but the top one will see most of the tensile force. the farther away the second bolt is the less tensile it will see so it would seem to me that it should be as close as possible to the first. but the strength of the concrete with 2 holes drilled in close proximity concerns me..
anyone with any thoughts... advise??
thanks
ralph
the farther away the second bolt is, the less tensile force it will see is right.  that is a good thing.  less force on bolts is good in this case.  the minimum distance between the bolts is that which will induce tension that, when combined with the shear, will overload neither the bolt itself nor the concrete to which it is attached.  
will you have some sort of bracing or something to make the bracket rigid enough that you will not also have forces due to the bracket moving out-of-plane?  
it is up to you to either calculate the forces and bolt capacities or hire someone who can.  we cannot do that part, of course.
anchor bolt manufacturers such as hilti have information on the minimum spacing between anchor bolts.  the spacing is typically governed by a pullout shear cone, so that the bolts are not within the cone of another bolt.
are you bolting the 50" horizontal part of the bracket anywhere?  that seems like a bit of a long span to go without any bolts.
thanks for the comments.
the horizontal portion will have a diagonal brace.. from 2/3 the distance (at a 30 degree angle.. mating with the vertical at 60 degrees. the bracket will be 4x4 x .375 structural steel angle, welded .. there will be 4 of these to support a 10 foot x ~50 inch wide addition to my house.. making room for a main floor laundry, part of which will be within the current walls.
the comment about "hilti" i will look into, but this is not quite like a pullout cone as i am drilling through.. and with a back up plate / washer..
ralph
how thick is the concrete you're anchoring to?  the top bolt will be in tension which will try to pull your anchor plate through the concrete.  the perimeter of the anchor plate and the thickness of the concrete will determine how much pullout force the concrete can handle.  
sounds to me your structure will be plenty strong enough, i would guess the top bolt should go somewhere near the top of the 24" l and the bottom bolt approx 12" below it.
thanks bagman..
the determining factor will be how close to the top of the concrete wall i can have the top hole.. tenativly i had thought a minimum of 8 inches.. then the next one 10 inches below that.
my basement wall thickness is unknown at the moment.. i am assuming a standard 8 inches.. which seems to be the norm around here.
you will still have a truncated pullout cone.  it just won't have a bottom.  this situation yields less trength than a bolt with a similar embed in thicker concrete.  the washer will be pushing on the back of the wall the same as a headed bolt would be pushing on the pullout cone in a cast-in-place application.  the washer size and wall thickness will determine how much cone you have.  so you still have to check the strength of the concrete as well as the bolt even though you have a through-bolt and not a typical anchor set in concrete.  
don't arbitarily set distances between bolts.  the distance between bolts affects the tension each bolt gets.  too little distance will give you large forces.  too much and you may adversely affect your frame.  
again, you should make sure you check all of your numbers thoroughly and sufficiently or hire someone who can.
thanks ucfse..
the "steel" numbers have been worked out and verified as being sufficient with ample safety margin...
but the.. "so you still have to check the strength of the concrete".. part concerns me. the only tests i have ever seen on concrete are essentially compression factors. how much sideways force a concrete wall can sustain is kind of an unknown as there are many variables which are pretty hard to quantify.
using simple geometry.. i assume a 1000 pound load at 32 inches from the wall then one bolt would have to hold 32000 pounds, if this bolt was lowered 8 inches the force would increase to 48,000 pounds (assuming a pivot point at the bottom of my 24 inch leg)which is not true as there will be another bolt to assist... but that calculation  exceeds my simple geometry skill...
there will be 4 brackets spread over 10 feet. my basement wall is ~30 feet long and a standard 8 feet deep. grade is some 12 inches from the top of the wall.the addition will be centered on this wall
my gut feeling is... the wall can handle it.
(should i be worried??)
if you have not done the proper engineering then yes you should be worried.  32000 lbs is a lot of force is it not?  we cannot say "no, don't worry it'll be fine" over the internet.  anyone who does is out of line.  that is a clear liability as well as ethics problem.  the advice i can give you is to hire a professional.  from reading your posts it seems you know just enough to get in trouble, but not enough to perform all of the required engineering calculations and judgment to do a thorough and complete job.  the amount of sideways force a concrete wall can sustain is only unknown until you check it with a rational engineering analysis using the proper building code.  then it becomes known.
again, you should make sure you check all of your numbers thoroughly and sufficiently or hire a registered professional engineer in your areafff"> who can.  if you are not a strucutral engineer yourself, and you do not have the proper knowledge to actually check everything and not just the few things you know, then you need to hire someone.  we're not going to check it for you or give you a "yay or nay".  that is neither our purpose nor the function of this site.
i agree with ucfse. you are not talking about a lot of investment for peace of mind.  you may also get a cheaper / better / easier way to do what you are trying to do.
zcp
i don't want to appear self-serving, but you should talk to an engineer about this.  he will need access to your home to inspect the condition of the walls where you want to make these attackments.  checking the steel is the easiest part because all that will be new.  assessing the capacity of what is existing will be the real trick.  one thing that has to be checked is the capacity of your basement wall in bending were you are making the attachment.
i think the guidance produced by the hilti corporation is worth reading for your first question, but i think there are questions that need answers of which you haven't even considered.
good luck.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2025-1-11 22:38 , Processed in 0.040593 second(s), 20 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表