几何尺寸与公差论坛

 找回密码
 注册
查看: 687|回复: 0

cant achieve hook development length

[复制链接]
发表于 2009-9-7 22:33:08 | 显示全部楼层 |阅读模式
can't achieve hook development length
hey there - what do we do when we can't achieve hook development length?  for example, a concrete column w/ #6 verticals sitting on a 14" deep footing.  the #6 hook development length for my condition is 17".  i can't get 17" into the footing and the footing can't be any deeper.  
thanks in advance
check out our whitepaper library.
look at aci 12.5.3
this gives you some options.
if all else fails, you cold provide higher strength concrete to reduce ldh.
btw, i don't know where you're getting 17". higher than any number i have.
can you get sufficient steel by using smaller bars? do the bars need to develop full strength or is part strenght acceptable.
you can also use a proprietary stress block at the end of the bar to take the stress.
did you multiply it by .7 or other factor according to 12.5.3?   
never, but never question engineer's judgement
thanks for the responses.
multiplying by .7 is something i will do to feel better... although i'm not certain that we will have the adequate cover required because this is being constructed in the middle east and there is no quality control.
and yes 17" is correct for our conditions. concrete strength is low.
i'm going to check the capacity again - i may have some wiggle room there b/c the moment designed for at the top is lower that that at the bottom and it's the same r/f.
i assume that you are trying to develop in tension and not compression. is this correct?
use more dowel bars to reduce the embedment by the ratio as provided to as required.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2025-1-12 13:25 , Processed in 0.039014 second(s), 20 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表