几何尺寸与公差论坛

 找回密码
 注册
查看: 465|回复: 0

concrete excavation

[复制链接]
发表于 2009-9-8 12:04:19 | 显示全部楼层 |阅读模式
concrete excavation
hello again,
i am trying to find areas of maximum internal bending moments in the walls of a concrete structure. the shape of the structure is a rectangular box and is quite massive (about 5m x 7m x 30m). the structure is underground and will experience varying pressures along the side walls. i have modelled this structure using an fea program but i also want to compare those results with hand calculations. what is the best way to approach this problem?
thanks
i don't think you'll find a simple, good solution by hand.
you can take each face individually, treat it as a flat plate, apply whichever of roark's formulas seems to fit the best, and check loading in that way.  check it assuming simply supported and with fixed edges, and assume your case is somewhere in between.
you can isolate a section out of the box, treat it as a square frame, and design for bending in that direction.
you can treat the faces as slats running in the short direction, check reinforcing in that direction, then treat as slats crosswise and check reinforcing in that direction.
roark may even have some equations for a rectangular tank which could be applied.
in any case, you may be able to come up with a satisfactory design by hand, but you could have some pretty wide variations between the design and fea model.
this kind of problem is vastly simplified in many cases when the reinforcement required by loading falls below the required minimum areas- then you can make some pretty appoximate, but conservative assumptions, and still have a reasonable design.
isn't this a relatively straightforward box culvert design scenario?  just consider a 1m length of box culvert unit and carry out an analysis for all the different loading combinations that you have, and design for the worst case bending moments and shear forces for the walls, roof, and base.
the reinforced concrete designers manual has worked examples for this type of design. (uk publication).
valleyboy
i did look at the reinforced concrete designers manual (not sure what publication) but i was unsure whether or not i could consider this a straightforward rectangular culvert due the massive size of the structure. though sectioning the model into 1m length box culverts may be a fair approximation. i'll try that out.
you should be able to check your fe results against the tables in this book