几何尺寸与公差论坛

 找回密码
 注册
查看: 518|回复: 0

construction joints in concrete

[复制链接]
发表于 2009-9-8 13:28:15 | 显示全部楼层 |阅读模式
construction joints in concrete
hi all,
is there any requirements for construction joints when designing water towers, shear-walls, retaining walls, slabs etc? the requirements that i have seen in aci/ubc-97 leads me to the "shear-friction" calculation. just taking into account the "shear-friction" calculation may we create construction joints verticaly in retaining walls, elevator shear-walls etc.
regards,
my short answer:  "yes"; control, construction & separation joints are necessary to all structures.  depending on how bit a structure is your control joints may simply be the ends of the structure, so given a small enough structure you don't need to introduce control joints, just show that they would be necessary at larger increments that the size of your structure.
you should look at aci 224.3r; "joints in concrete construction"... it has various chapters on a variety of different structures and elements.  i have found it to be an authoritative and useful document.
hi ys,
i completely agree with you about control and seperation(dilatation) joints. as long as they allow the free-movement(depends on dof of joint) of super-structure due to the enviromental effects.
what i intended actually to be answered is: for the concrete that we couldn't cast monolitically because of
huge amount of concreting area (slabs, walls, columns etc. ) may we make the vertical construction joints even
if we are in highly risky seismic zone and have to get stuck strictly with prescriptive code?
i got the copy of aci 224.3r and it doesn't mention the seismic loading.