crack control for rectangular concrete tanks

[复制链接]
发表于 2009-9-8 14:17:33 | 显示全部楼层 |阅读模式
crack control for rectangular concrete tanks
i have been using the pca rectangular concrete tanks book to design some wwtp tanks, as well as, other tanks.  i have developed some questions based on the procedure.  i am looking for others experience to get a feel for the final design.  
my concern is with the crack control req'd steel.  i am required to maintain 3 5/8" cover on the steel when i compute the stress in the steel.  this is due to the deneef swellseal bead to protect the steel at the cold joint and make the tank water tight.  the bead requires 3" of cover and the bead is to be 5/8" in order to maintain a waterproof joint.  because of this, my max spacing for the rebar to control cracking ends up being less than 4" (unreasonable).  the only way i can see to fix this problem is to increase the size of my wall or reduce the cover on the steel.  my tank is a small 12'l x 8'w x 12'h tank.  i have been trying to maintain a 12" wall.  it just seems excessive to increase the wall thickness to 1.5' just to increase the steel spacing.  
the other problem i have is the buoyant force.  the wwtp is located on the side of a hill, so i don't see how the soil could become saturated long enough to lift the tank, but the calculation shows that my fs is less than 1 and i have to increase the walls and slab to be huge to get the f.s. to even be 1.  i don't see any other way to make the tank heavy enough to resist the buoyant force.
so, i guess my question, on this small of tank, do you go to the extent of installing helical piers or is there other justification for resisting the buoyant force?  also, is my crack control spacing out of control?  i just need a feel for good practice to know whether i am not trying to make the tank too small, and should be looking at thicker walls, slabs, etc.  mass concrete or economy?
thanks for your comment/sorry for the long explanation!

if you have more than 2" clear cover, use 2".
use 2" in crack control cal. (if i re  
put the bead where it is required to be and the steel at 2" cover.  why put the bead outside the steel?

for uplift, i would try to make the base slab larger than the perimeter of the wall. draw a line (35 deg from vertical - consult w/geotech at final design stage) and include the enclosed soil weight. automated drainage system (sump pump & drainage fabric) may be helpful, but failure-prone (fabric could be clogged by fines that restrict flow, power outage..etc).  
perhaps helical anchors could be used to resist buoyant forces?  cost is ~$1500 each.  
additional weight of concrete might end up being more economical though.
so, kslee 1000, i can still use 2" in the calcs even though it is more like 3 5/8"?  
for civilperson, i would like to put the swellseal bead in front of the steel to protect the steel at the cold joint at the bottom of the wall.  however, maybe i am being over conservative.  i am assuming that the wastewater from the tank would leak into the cold joint and corrode the steel away.  am i correct in my thinking?
cuels:
yes, that was our practice (for water retention projects). i remember there was a paper discuss that, unfortunately, i don't have a copy on hand.
the argument above is similar to the aci consideration of "architectural columns" vs "structural columns". the excessive area serves a function but structural. hope this helps.  
concrete is not water proof, even with no cracks.  the normal cover and density has a permeability to moisture that allows small amounts of water to transverse the thickness of the wall.  this amount is not determental to the steel reinforcement since the initial coating of oxide prevents further corrosion.
i have no intention to debating reinforced concrete behaviors, there are many knoweledgeable persons handle that. just want to point out the fact that water tight (actually dense - low permeability) concrete has been widely used in water front projects for many years. to counter buoyancy, and for better protection of reinforcing steel, the structures are usually massive with clear cover arranged 4"-6". that's the reason we investigated, and determined to use 2" for crack control calculations. we provided concrete keys/grooves and continuous water stops along all construction joints to lengthen the path of seepage. some of projects (submerged powerhouse) are more than 30 years old, i haven't heard any structural problems yet. please note the reinforcement were plain grade 60 steel, no coating, and no water proofing was applied inside or outside.