deflection induced moments in struts bs5950
does anyone know of any guidance given in bs5950 (or anywhere else) about the level of deflection in struts (say horizontal roof bracing) before i have to add extra moment due to compression in the member acting a distance from the original centreline of the member.
not a direct answer, but the attached shows the reduction of compression capacity with increasing length, for a selection of shs struts.
it shows that deflection due to self weight is significant for effective lengths between 2 to 4 m, for the shs sizes shown.
capacity design was done to as4100.
if my memory serves me correctly, the old version of bs5950 did have a clause which gave guidance on this. compression   
you should always check this until you have enough experience to know otherwise. it is always amazing how much a little bit of self weight reduces the axial capacity.
thanks all