几何尺寸与公差论坛

 找回密码
 注册
查看: 481|回复: 0

dowels 2 sog

[复制链接]
发表于 2009-9-8 19:30:30 | 显示全部楼层 |阅读模式
dowels @ sog
i was in a discussion with a friend earlier tonight and we disagreed over what is allowable with regard to dowels exposed in a section of sog that will serve to connect to an additional port of sog to be poured later - no set timeframe.
i say dowels are acceptble so long as they are not scaly with rust or lose cross sectional area. he says dowels must be installed via a hilti epoxy.
this is a discussion about a residential outbuilding, and i have realized i am not very familiar with residential codes as he says they are very different than ubc codes.
anyway, i am in georgia, anyone want to shed any light?
thanks,
daniel
find a job or post a job opening
i don't think i understand your question since i don't see how your two points are at odds with each other, they seem unrelated.  what exactly is the question?
either way will work.  you can put the dowels in place, leaving the future section exposed (but before you place the concrete in the future, cover the dowels with tape and grease them so that they slide (assuming you want your dowels for load transfer)), or you can drill holes into the formed surface and set dowels in epoxy.  that's more labor intensive though.  plus, it you only want the dowels for vertical load transfer, no need to epoxy them after drilling.  let them slip.
if you are tieing two slabs together for continuity, you may do it either way, it's just easier to set dowels while placing the concrete than to epoxy them later.
exposed dowel bars, given the open-ended timeframe for pouring the second slab, might be considered a safety hazard - particularly on a residential site.
i'd recommend drilling and placing the dowels at the time of the slab extension.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2025-1-16 02:35 , Processed in 0.035871 second(s), 20 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表