几何尺寸与公差论坛

 找回密码
 注册
查看: 543|回复: 0

field fix glitch in manufacturing plate girder

[复制链接]
发表于 2009-9-9 11:41:12 | 显示全部楼层 |阅读模式
field fix: glitch in manufacturing plate girder
i'm working on a project where the wrong size plate was used for the web during the manufacture of some plate girder columns. these columns have already been fabricated and shipped to the jobsite.
apart from all the acrimony and finger pointing that is sure to occur; i want to have understanding of the different options available to increase the shear carrying capcity of a plate girder.
in a case such as this, is it okay to include the flanges in computing the shear strength of the member? if so, how would the contribution of the flanges be calculated?
any other ideas, suggestions or comments would be more than welcome.
thanks.
js.
check out our whitepaper library.
the shear capacity is (vq)/(it) and for w shapes v/dwtw is a good approximation. one option is to compute the shear capacity based on the above eqation. the other is to allow a slight increase if the capacity is close if you are using allowable stress. aisc tells you that the basis for fv=.14fy is old and very conservative. otherwise you will probably need to put shear plates on the web. is the axial capacity of the column sufficent?
first let me start by saying that i sympathize with you. it is not fun when such things happen! i also would like to applaud your action by wanting to find a solution and not dwelling on the acrimony of whose fault was it. we need to do what is right and keep public safety the number one concern.
i am assuming that you are using aisc specification for the girder design. it has been my experience that steel   
this link is a great one. it has welded plate girder chapter from ohio state university.
the plate girder applet is great. the link is in the bottom of the page on the link above. it is easy to use with good documentation. verify results!
regards,
lutfi
i think more details would be needed for specific answers.
your allowable bending moment will be reduced slightly as well.
in some cases, you could add stiffeners to the web to increase shear capacity- depends on what governed the design in the first place.
the design codes are always written in terms of minimum specified yield strength.  actual yield strength, as shown on mill test reports, will run several ksi higher.  if it can be approved by all concerned (and that's a big if), you could redo the design using actual yield or tensile strengths.
who designed the beam?  get them involved if they're not.  there may be some inherent overdesign included.  they may can remove some approximations and reduce the required strength.
depending on the configuration, you could possibly weld a strip of plate on the web, near one of the flanges.  fair bit of work, but better than scrapping the beam.
you may want to revisit web crippling also.
lufti, thanks for the link. it seems to be filled with a wealth of great info. i'm sure it will come in handy.
a little more background: due to space constraints, we were forced to use a shallower column than we normal and as a result, the thinner web plate does result in overstressing the   
could you take some round bar and bend it in the configuration of a warren truss web and weld at panel points to the flanges similar to an open web joist and neglect the web plate? are web stiffeners in the way?