loads on floor hatches

[复制链接]
发表于 2009-9-10 11:23:39 | 显示全部楼层 |阅读模式
loads on floor hatches
hi all,
i think i have asked this before.  i am looking for a formula to calculate safe loading on aluminum plate floor hatches to arrive at the plate thickness and the bearing area required on each of the four sides.  these hatches are subject to vehicular traffic of varying weights.
i do not have access to references such as rourke's
thanks in advance for any help.
check out our whitepaper library.
in the case of plates supported along fouir edges, the proportionate load carried by the short span is approximately:
    p = b^4/(a^4 + b^4)
p = porportionate load carried by short span
a = length of short span
b = length of long span
when b/a > 1.5 design as one way
best