几何尺寸与公差论坛

 找回密码
 注册
查看: 449|回复: 0

maximum load on beam

[复制链接]
发表于 2009-9-10 13:20:59 | 显示全部楼层 |阅读模式
maximum load on beam
what will be the approx. maximum load on a 4"x6" wooden beam, 14 ft long, when downward pressure is applied in the center of this beam?
the beam 7 ft high, supported at 2 places by 6"x 6" posts 14 ft apart.
the beam is laid down with the 4" side resting on top pf the post.  
that depends on the species of wood and grade of wood.
to jca, thanks for the quick response.
in reply to your comment, this 4"x 6" beam is pressure treated pine (.40 cca i guess) for outdoor use.
maximum (safe load for a good quality member) would be about 500 lb. which would give you bending stress of about 1200 psi, minimal shear, and 3/4 inch or so of deflection. fourteen feet unbraced length should not be a problem for this size wood beam.
if this is for the swing that you mentioned in your previous posting, i would reduced that to 400 lb. since you could have moving and impact loads plus safety issues.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2025-1-20 03:27 , Processed in 0.037243 second(s), 20 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表