几何尺寸与公差论坛

 找回密码
 注册
查看: 470|回复: 0

remove bearing wall in residence and install adiquate suppor

[复制链接]
发表于 2009-9-15 17:53:15 | 显示全部楼层 |阅读模式
remove bearing wall in residence and install adiquate suppor
i have a bearing wall that i would like to remove.  the wall supports 2 floor joist spans.  1 span is 10 linear feet and the other span is 21 linear feet.  i would like my beam to span 16 feet with a steel support post on each end.  this structure is a 2 story house and would like the downstairs to be open completely.  i already have a footing under the area i intend to place my posts.  i need help determining the size i-beam and support post i will need to carry this area.
these things are always to be made with extreme care. parts of the building that are not intended to behave structurally do so, and as well take part on the lateral stability when not intended so. so my best advice is to commit the reform to one with experience in such works.
now, your problem is as easy as to calculate a simply supported beam for the proper load and at very low deflection. proper end connections, columns, and footings are also required.
my recommendation is not to exceed l/1000 total service level vertical deflection, especially if the bearing wall continues above, in which case l/1500 would be even better maximum deflection. if no bearing wall above, you can relax to maybe l/500 if you are ready to take some minor cracks in your structure.
also, when designing your columns, don't forget to note that the loads are applied eccentrically, at the bolt line. it is not a centered load in the column.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2025-1-16 04:54 , Processed in 0.037670 second(s), 20 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表