shortest bar joist
what is the minimum span length barjoist manufacturable?
thanks!
tables for k-series start at 8 feet. use joist substitutes, small beams, channels or tubes for 10 feet or less. refer to vulcraft joist catalog.
look at using vs joists.
use hot rolled steel sections. they might be more readily available from local warehouses/steel shops. if you have lots of steel joists on the projects, them use vs joists as suggested above.
another alternative, depending on loading, is cold-rolled steel sections - c and z light gauge purlins.  they are lighter than the standard roll sections, therefore easier to handle in the field.  you do have to be more careful with lateral bracing and connections.  just a thought!
another alternative, depending on loading, is cold-rolled steel sections - c and z light gauge purlins.  they are readily available, lighter than the standard roll sections and easier to handle in the field.  you do have to be more careful with lateral bracing and connections.  just a thought!
make sure you proceed with caution when using vs joists depending on the fire rating required if applicable. vs joists at this time are not u.l. rated.