truss alteration, consequences in fl building code?
i bought a new house in fl, newly built, had it inspected and noticed a truss that was altered beneath a master bathtub to give way for the drain pipe. is this action within the residential building code of fl, if not how should this be fix and what documentation should i ask from the builder to assure that they repaired/modified or fixed the alteration? help please.
check out our whitepaper library.
sounds like you are discribing a floor joist. typically fabricated residential joists are 2x4 syp open web design in florida. what is the joist design, and the stage of construction?
typically trusses and fabricated joists in florida are engineered. the company that provided them have provided a profesional engineered (pe) design. very few modifications are permitted to the joist. if modifications are made the builder is required to obtain an engineered design (usually from the joist fabricator). both the joist engineering documentation, and florida law require it. consider talking to the builder as your contract is with him (he contacts the joist shop for the allowable redesign).
hope it helps, cheers
boo1
it depends on how it was altered as to whether or not it is a structural issue. as boo1 said, ask the gc for the documentation on the floor truss modification from the design engineer. if none was obtained, that's a flag. require the gc to get the design engineer to check it and make a decision....either ok as is or provide fix. either way a document must be obtained from the engineer. if the gc balks, tell him you want the documentation from the local building inspector (or could have been a private provider inspector in florida) that it was accepted or you will notify the local building official of the issue.
thanks ron and boo1,
actually i got a copy of the truss repair info from the county building inspector. however i'm still wanting to have a letter that states that it was fixed according to code -(do you think i can get this?).
when the county inspector did the framing he overlooked at this issue. and then when i went there for the initial walk thru i asked the builder if this issue was taken care of, he told me that everything that needs to be done has been done. i asked for the documentation about the engineer's approval and he can't provide it. this prompted me to make a follow up with the county inspector. the inspector then told me that he went back there (unit) and saw the builder ripped the ceiling and modified the alteration based from the pe's recommendation. i'm doubtful with this one, since they lied to me before, what do you think will be the best approach for this? right now i'm just asking for a certification letter that they fixed and repaired the truss issue. who else should i notify aside from the county inspector?
one more, i called the florida building commission and asked them about this, and they told me that i've the right to ask for it.
test24...certainly you have the right and the building official should be asking for the same "sign-off" from the engineer.
you need a letter from the engineer stating the problem, giving the fix, and then stating that the fix was done in accordance with his recommendations. get the gc to provide this and if he doesn't, complain to the florida construction industry licensing board (cilb). the have a complaint phone line.
here's their web site....
you may need to go higher than the county inspector's office.
i suspect the inspector was lax, and now you're essentially putting the inspector and his office on report, as well as the general contractor (i'm also a little suspecious of the overly "cozy" relation between many inspectors and contractors, but that's just me).
can you get any documentation from the truss manufacturer/designer, that will support your claim that the truss was not properly repaired?
also, assumeing the house is mortgaged, consider going to the mortgage company. they have an obvious financial stake in your residence and may provide some assistance.
otherwise, the last resort is retain an attorney and find out who you need to take to court (which may be tricky because you may end up opposing the county inspector's office).
ron , mshimko
the county inspector admitted that he probably overlooked at this issue. he apologized and recognized his error. i sent a letter to the county building department and made them aware of this issues and told them not to issue any co until this matter has been resolved. i feel that both the gc and county inspector had their share, i spoke w/ the builder (agent) mid december and asked her if the truss issue has been resolved and she said yes, negligence is what they did at 1st. if i didn't push for this, they will not do anything about it. is the contract null and void if they didn't follow the state law? is the residential building code a law that needs to be followed?
first, any alteration should have been done in full complisnce with the local code or the adopted version of the ibc. second, i believe that the code becomes the law only if it were adopted by that state.
can you better describe the fix? the type of damage described happens fairly often (gotta love them plumbers)and can be readily fixed. in fact, most truss companies have "standard" repairs they send out in these cases. i am not necessarily trying to say what you have is a non-issue, but it just may not be that big of a deal.
regarding the description of the "fix", first a description of the damage would be helpful.
it sounds like the top chord was cut or notched. that reduces the size of the member. it may or may not be overstressed as a result. in either event, it will be important that a qualified engineer has examined the extent of the damage, evaluated the loading on the truss and the forces in the members and determined what if any reinforcements are needed.
key descriptions are needed for the amount of original material that was cut away (how big is the notch ) and where the notch is located. is anything cut out from any of the web
yup, it's a plumber special. truss is under the master bath (2nd flr) a piece was notched to give way for the drain pipe. the builder is refusing to issue a letter that certifies a fix/repair was done. there was an engineer recommendation on how to fix the truss however no assurance that it was done base from his recommendation.
if this is not a big issue, how come the gc is refusing to issue any certification or any letter that it was done w/in the code or in accord the engineer's recommendation?
in florida, is the building code a law? |
|