几何尺寸与公差论坛

 找回密码
 注册
查看: 563|回复: 0

wet set dowels in concrete

[复制链接]
发表于 2009-9-16 20:09:46 | 显示全部楼层 |阅读模式
wet set dowels in concrete?
what is the thinking on wet setting straight reinforcing bar dowels into the tops of foundation walls for masonry anchorage?
i think the precast section of the aci allows it providing there is no hook or anchorage to other items and that displacement of the dowel is prevented and proper consolodation around the dowel is provided.
can that train of thought be applied to cast-in-place work too?
it seems that much more material is required to tie widely spaced dowels in the forms before casting, adding expense.

does the foundation wall fall under the irc or the ibc?
if it is a residential basement, the dowels may not be required unless the wall is a cantilevered wall.
if you are under the ibc, there are different rules and cannot use the proven methods that work for the qualifying applications.
to answer concretemasonry:
ibc but whether required or not is not the question as it is engineered masonry and they are not optional by design.
to avoid confusion, the dowels are in tops of concrete foundation walls for masonry superstructure anchorage.
aci 318 states all reinforcing must be accuratly placed and secured against displacement prior to placing concrete. aci 318-02 sec 7.5

curious why aci 318-02 sect 16.7 allows wet placed items.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2025-1-10 03:49 , Processed in 0.037685 second(s), 20 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表