wwr designations & charts
does anyone know where i can find a good online resource for explaining welded wire reinforcing designations and spec information? i have a small sog, but i don't want to use rolled wwr for obvious qc reasons.
thanx in advance.
kelly lyons, pe
principal
just call out w6x6-2.0x2.0 flat sheets
i dont know an online source but im sure a lot of people have a table. post the area of wire per sq. ft. you want to spec and we can give you the designation.
try the wire reinforcement institute, here is a link:
this brings up an interesting question that i have meaning to ask. i don't think it is off topic.
6x6 w2.0xw2.0 is listed in the chart slideruleera listed above and in my aci 318. now i specified that a couple times and the contractor came back and told me they could only get 6x6x w2.1xw2.1 which is not listed in the charts.
now i went back to some references my boss had from 20 years ago and he had crossed out the 2.0x2.0 and replaced it with 2.1x2.1 and many drawings we have use this.
i am confused that what is in the chart is not what people can get
anyone help with this?
ive never seen or heard of 2.1x2.1. i was trained by an older engineer and we used to still spec it as 66-1010 or 66-88 and i still spec using the old designations out of habit and ive never had a question. |
|