wood stud wall backing brick veneer deflection limitation

[复制链接]
发表于 2009-9-16 23:14:22 | 显示全部楼层 |阅读模式
wood stud wall backing brick veneer deflection limitation
does anyone have a code reference for deflection limitation for a loadbearing wood stud wall backing brick veneer?  thanks.
check out our whitepaper library.
what code are you designing to?  bia suggests a deflection criteria of l/600.  ibc states l/240 for brittle veneer.  which ever criteria you use, the ibc and the fbc let you multiply the lateral load by 0.7 when calculating deflections. hope this helps.
j
i should clarify lateral load due to wind.