0.6 conform deck as diaphragm - er report
is there a 0.6 conform deck that has diaphragm shear values that complies with an icbo/er report?  the deck is designed as a rigid diaphragm using concrete on top of the metal deck.  vulcraft has design tables but no icbo reference.
i do not think you will find any data on the deck by itself. however, if you have concrete placed on it, then you will have rigid diaphragm.
my sdi manual is at the office and i will look it up.
regards,
lutfi
if you're asking for the "bare" deck, sdi manual has diaphram values for no fill.
i am specifically looking for design values with a concrete deck
i'm not aware of any icbo/er reports available for form decks less than 1 1/2" deep.  i couldn't find any on the icc/er website.  sorry.
you will have to calculate it using sdi which isn't very fun.  this program will do the calculations for you.