foundation with two way eccentricity
i have a column with uplift and horizontal reactions in two directions at the base.  i would like to size the footing to resist the uplift and keep the dimensions as small as possible.  i have a copy of principles of foundation engineering by braja m. das that i am using to calculate the effective bearing area and soil bearing pressures.  my question is, besides the bearing capacity of the soil, what else should i be concerned with in sizing the footing?  at what point does this become unstable?  do you think that the footing is acceptable as long as i maintain an adequate factor of safety against overturning on the individual footing?  say (otm)/((ftg wt) x ftg length/2)) > 1.5
also maintain an adequate factor of safety against sliding.
daveatkins
keep your resultant within the kern distance.
not necessary to keep within the kern - as long as the bearing pressure under the reduced bearing area is acceptable.
i usually look at eccentrically loaded footings similar to a retaining wall foundation which that book you have cover very well. you have max bearing pressure at the "front" to check(two dirs in this case). uplift on the "back". overturning. i doubt sliding will be an issue if you dont have lateral force. besides that, the footing itself needs to be designed. for this, you probably should look at a concrete book.