几何尺寸与公差论坛

 找回密码
 注册
查看: 435|回复: 0

ibc table 1604.3

[复制链接]
发表于 2009-9-9 18:55:39 | 显示全部楼层 |阅读模式
ibc table 1604.3
with c&c wind loads, the ibc 2000, now has a 0.7 factor that you can use in association with table 1604.3, for deflection limits. since brick deflection limits are not listed in this table, i assume that we are not allowed to use this reduction factor when calculating deflection for brick venneer with metal or wood stud backup.
is this how others are interpreting this?
i would consider brick a brittle finish. you could justify it also considering the interior finish on the studs likely being wallboard. then use the 0.7 c&c wind load reduction to limit the deflection.
您需要登录后才可以回帖 登录 | 注册

本版积分规则

QQ|Archiver|小黑屋|几何尺寸与公差论坛

GMT+8, 2024-11-16 03:33 , Processed in 0.163494 second(s), 19 queries .

Powered by Discuz! X3.4 Licensed

© 2001-2023 Discuz! Team.

快速回复 返回顶部 返回列表