masonry retaining wall - reinforcing ?
i am designing a 12' high ret. wall.  the block's f'm=2000 psi.  it's 12" retaining wall block which is the type with grooves cut into it for horizontal reinf.  my reinf. steel's fy=60ksi.  i called out for #8s @ 8" for vert. reinf. 3" from the soil side.  the contractor wants to use a lesser bar.  i have the horizontal reinf. i can tie to.  anyone see a problem with calling for (2) #6s in each cell at the same location as the original w/ 3" between them?  i am using special inspection and am going to make them tie to the horizontal steel to maintain this distance
check out our whitepaper library.
if the reinforcing is lap spliced, which it will likely be  for a 12 foot tall wall, you could have a few cells with the equivalent of 4-#6 bars in a cell.  add this to any hozizontal bars you may have in the grooves, and it doesn't leave a lot of room for grout!
in my opinion, using (2) #6's in a core is difficult.  with 12" cmu, the cores are about 6" x9".  trying to get grout arond a single bar in a cmu wall is difficulkt.  trying to get grout around (2)#6's vertical + (2)#6 dowels or splice bars will be next to impossible.  stick with the #8's
better yet, switch to a concrete wall, you will probably cut the reinforcing steel required by a 1/3.   
definitely keep it to a single bar per cell for ease of placement and grouting purposes.