metal building foundation.
i am trying to design a slab on grade for a metal warehouse building. this slab also needs to act as foundation for column vertical tension and compression loads.  this is my first time designing a foundation like this. i would like to know, how the moments due to these vertical loads can be closely calculated?
also, i shall appreciate any other design consideration.
check out our whitepaper library.
i think most folks would thicken the slab in the vicinity of the column, creating something that looks like an integral spread footing.  then design this footing like you normally would.  this isn't the only way to approach the problem.
i dont think you can use the slab for your vertical loads, for vertical loads you need to increase the size of the slab below the columns, and design this specific portion just like you would design a regular pad, u can use the slab on grade for horizonzontal thrust. but be carefull that in case of wind load you will get uplift on your column footings, so maybe the increase of slab size under columns becomes un-practical and you may need soil cover on top to prevent uplift.

thanks for the responses.
i have a large uplift force in the column. so, i have to size the footing to handle this uplift. the thing is, the moment generated in the footing due to this uplift is nothing compared to the size of the footing. i was trying to find out a rationality in aci-318 behind having the footing unreinforced.
i have a 8 kips uplift in the column, which requires a footing size to be 4'x4'x3.33'(deep). by the way, the down ward force on the footing is only 6 kips. can i have this footing unreinforced?
zaes73 - i don't see why you think you can't use your slab for vertical loads.  271828 was correct in that you will thicken the slab at the columns so that it can take the vertical forces/reinforcement. it is done all the time. - a thickened raft slab.  as for your uplift, why not install screw piles below your foundation to take the uplift?  that way you don't have to go to strange lengths to handle the uplift load.  you will have to put in the proper reinforcement to integrate the screw pile top into the foundation.
4 x 4 x 3.33 is not unusual for a metal building footing - i have these all the time - just pour monolithically with the slab.  as forbeingunreinforced, as i am in a seismically active area, i would always provide theminimum reinforcing.
mike mccann
mccann engineering
i feel a lot more comfortable using a wall foundation that's independent of the slab-on-grade. this kind of foundation is sized for uplift, etc. uplift is always a problem if the building has potential to be partially enclosed. re: reinforcing - start with the minimum required, perhaps that will work just fine.
msquared48,
for footing, the minimum reinforcement is .0018ag. i like to divide this total amount in two halves and provide half close to the bottom and other half close to the top of the footing. i do not want either top or the bottom of the footing unreinforced, nor i want to provide any more total reinforcing than minimum required.
can you please comment?
shin-
we have had numerous discussions on the 0.0018 min.  that should be provided on each face, not 0.0009ag on each face.
"we have had numerous discussions on the 0.0018 min.  that should be provided on each face, not 0.0009ag on each face."
i don't agree! (couldn't resist))
shin,
i don't see why you wouldn't use a portion of your slab to resist uplift.  if you are using a hairpin for horizontal rx, it must be integrally tied around the column anchor bolts, so i see no reason that you wouldn't at least include the weight of the chunk of slab covered by the hairpin to add to your uplift resistance.  also, we typically use a pier on top of the spread footing connected with a couple of zee bars (reinf bent into a zee, or zed) to tie the footing and pier together.  this way, you can keep the footing thickness to a minimum.  as well, we direct the continuous turn down footing bars adjacent the column footing to run through the back of the pier, which also increases the uplift resistance.  hth.
peggy