metal stud and gyp wall movemen

[复制链接]
发表于 2009-9-10 13:44:23 | 显示全部楼层 |阅读模式
metal stud and gyp wall movement
hi,
i have a project were the gyp sub attached the walls to metal building columns. we required that they maintain space around the columns to allow building movement. the question-are there any guidelines for allowable movement in gyp board walls? the walls are both parallel and perpendicular the column frame movement. thanks
u.s. gypsum's "gypsum construction handbook" gives this info.  it requires relief joints at all columns and control joints for every 30 feet of wall.  go through the book to get the exact references.
it is available directly from usg.  you can order it in print or get a free pdf copy of it at: