modification of existing bar joists
need some help/advice with the following situation proposed an architect. a new elevator shaft and stairs are intended to be installed within an existing 3-story, 25 year old building. framing system is 18" 'h' series bar joists @ 24" o.c. supported on exterior 4" brick/4" block (i'm assuming composite) w/ 4-1/2" concrete on decking.
the plan at the elevator is to build the shaft up thru the vertical space while the joists are left in place (removing the concrete and decking within the shaft space) and then provide some sort of connection/stiffening of the joist at the masonry walls. after the joist is supported the joist within the space can be removed.
the stair would be supported on new steel beams which would also support the existing bar joists, also cut back.
has anybody done anything similar to this before. i do plan on contacting some joist manufactures and possibly sji but wanted to get some other opinions, too.
thanks in advance.
check out our whitepaper library.
if you cut or change the joists in any fashion, you will void the manufacturer's warranty on the product.
i strongly suggest going to the original manufacturer, if available, and involve them in the changes. if they are out of business or not available, the sji is a good start.
mike mccann
mccann engineering
msquared48, i doubt that a 25 year old building still has a warranty of any kind, wouldn't you think?
we've done this numerous times. fairly straightforward.
plot the joists shear and moment capacity diagrams (re
jae:
thanks for the reference.
more than likely you are right, but i would still check it out first. strange things do happen...
mike mccann
mccann engineering
as jae said, we have done this sucessfully numerous times. i recommend a site visit to field measure the joists including panel points locations. this may affect how the reinforcement is detailed since all joists are not manufactured the same.
i've run into this situation a number of times....
field measure the joist.
analyze the existing joist as a truss
analyze the new configuration as a truss.
thanks for the replies, you've all reinforced what i was thinking. it all seemed fairly straightforward, i just wanted to make sure there wasn't anything obvious that i was overlooking. |
|