post-tensioned flat plates

[复制链接]
发表于 2009-9-15 13:52:46 | 显示全部楼层 |阅读模式
post-tensioned flat plates
does the aci code or bs standards allow tendons to be distributed equally both ways without the need to provide them in bands in at least one direction?
from my reading of the aci code and concrete society technical report no. 25 which is based on bs standards, they seem to allow it.
can somebody clarify the above for me?
thanks

hi,
   you question needs some clearification...but for answer is avaiable on a website :-
aci would allow the tendons to be uniformly distributed in both directions. the problem with doing that, however, is that it will make the placement of the tendons quite complicated. when tendons are banded in one direction, the banded tendons can be laid out first, and then the distributed tendons laid out over the band. when the tendons are arranged uniformly in both directions, they have to weave among each other.