rho minimum = 0.0018 x hf / ( 2 x d), where hf = height of footing and d is hf-cover. is this formula ok as per aci 318-05 for minimum steel to be used in concrete retaining wall footing.
find a job or post a job opening
no, no width term shown and footings can be designed as plain structural concrete.
crown06-
i don't know what you mean by that formula, but i use the rho of 0.0018 for the min.  just multiply it by the hf*12 for in^2 per foot.  
civil person-
i've always wondered about plain structural concrete.  if, for reinforced concrete, you need t&s steel to prevent cracking, how do you prevent cracking in plain concrete?  i would think that it would be a very bad thing if a plain footing cracked near the critical moment section (due to shrinkage), thereby reducing the effective s for the footing and causing it to fail.
eit, check out aci 318 22.3 code and commentary.