shear capacity of gypsum board

[复制链接]
发表于 2009-9-15 21:32:42 | 显示全部楼层 |阅读模式
shear capacity of gypsum board
does anyone know of a good reference or tables for the shear capacities of gypsum sheathing and gypsum wall board on wood wall studs?  the ibc 2006 has one table (table 2306.4.5), but it hasn't been of much help for me.  do any gyp board manufacturers have a website with that kind of info?  any help is much appreciated.
check out our whitepaper library.
why doesn't that table in the ibc work for you?
the australian timber framing code as1684 gives the following bracing capacities for nominally fixed plasterboard walls:
one side sheeted - 0.45 kn/m (30 lb/ft)
two sides sheeted - 0.75 kn/m (50 lb/ft)
well, i am actually checking the design of an existing facility, and the spacing of the studs are different as well as the nailing pattern than what the table has.  there is also sheathing on both sides.  intuitively i was thinking you could just double the capacity then, and i was mutiplying the table capacities by the ratio of the stud spacing.  but, i'm not sure if this is really correct, so i wanted a reference to see if these assumptions were correct.