solving for impact loading

[复制链接]
发表于 2009-9-16 00:32:56 | 显示全部楼层 |阅读模式
solving for impact loading
i am doing an overhead steel beam that will have a fall arrest system that will run along the bottom flange of the beam.  how do you determine the actual force?  up here in canada we used to have a factor of 1.65 for loading lasting less than 10 min.  this is a project for the us.  
basically, if a 200 lbs man fell what would the force be?  would it be as simple as f=ma? or is there a factor to use?
thanks
check out our whitepaper library.
i believe we typically use a load of 1.5 kips in any direction.  you can lower it if you meet certain criteria, but that is a good starting point.