in one of our job, the contractor wants to construct the walls/columns without kicker (75mm).
it gets me question that the pros and cons of kicker / kickerless method of construction
cheers
kickerless seams fine to me but edge columns should i think have them as its safer (helps locate the columns shutter so it cant slide of an edge as it were).
if you omit kickers at certain locations where you have a knuckle joint condition in the wall, it creates structural instability.
therefore, if you chose to go along with the contractor, you will have to maintain the stability of the wall another way.  good luck.
mike mccann
mccann engineering
what is meant by "kicker"?
i think most contractors try and avoid kickers and i do sympathize with them.  there is alot of fiddly work in making them.  mike what is a knuckle joint?  first time ive come across this term.  i always thought kicker or kickerless is structurally the same.
cheers
i'm with civilperson.  would appreciate if someone would explain "kicker" to him and "kickerless" to me.
a kicker is a starter on a wall(from the footing) about 50mm high so that shuttering (formwork) may be started for the vertical placement of concrete.  its more a construction feature than a design feature hence my comment above.
cheers
a "kicker" is a term for a diagonal brace to a stud wall (pony wall more than likely), where the stud wall is framed above a concrete wall.  the concrete wall retains earth and does not have lateral support via a floor diaphragm at the top.  this kicker serves to transfer the lateral pressure from the soil to the floor diaphragm above. the kicker does not have to frame to the top of the concrete, but may intersect the studwall at a position between the top of the concrete wall and floor diaphragm.
the "knuckle joint" i refer to is the joint(at the sill plate) between the top of the concrete wall and the pony wall.  this joint has no fixity to resist the soil load, so it is treated as a pinned joint.  this condition is not critical for yielding walls, but can be critical for non-yielding, or basement walls that are not full height.  that is why i refer to the condition as a "knuckle joint".  
sorry if i mislead anyone here.
mike mccann
mccann engineering
just as i thought, the word can mean different things to different people.  but now that i think about it, i have hear the starter hob called a "kicker".  just didn't re  
thanks mike
maybe i got my terminology wrong.  my apology if i misled, i was thinking of what we construction people call kickers or starters and this is different to what you have explained.
cheers
thanks for all your input.
though this is not a design feature, it would be helpful in construction.