bottom flange connection
bottom flange connection
what are your opinions on underhung, or bottom flange connections? is it acceptable to support a beam by a column that is supported or hung from the bottom flange of a beam above? thank you! if i understand correctly, you are hanging something on the bottom flange of a beam. make sure you check the flange local bending and web local yielding of the supporting beam --- in addition to the overall capacity. this would be chapter k of the aisc specification. with hanger-type structures, add an additional factor for impact or hanger loading as it is not redundant. yes it is acceptable if i understand you correctly. i would not call i t a column tho, i would call it a hanger. also when you have connections like that, pay close attention to the prying action of the hanger connection on both ends. by the way, i have designed an entire mezzanine without any column because the client wanted a clear open floor free of columns. i had to suspend the entire mezzanine floor from the rood structure above. good luck. |