girt deflection calculation 9pre-engineering building design
girt deflection calculation (pre-engineering building design
hello everyone, for the pre-engineering building, when we calculate the girt's deflection under the wind load,(cold formed steel and clading system) which should we use to check the deflection, l/360 or l/180? thank you very much! best regards, tom check out our whitepaper library. if the girt gives lateral support to steel wall panels only, l/120 is acceptable. if the girt gives lateral support to cmu, i would use l/360. daveatkins i use l/600 for masonry support. if you're designing the mbs, you should look in the building specifications and contract documents first, then the mbma manual, if you're in the us. |