ieff for composite steel beam
ieff for composite steel beam
can someone point me to a reference on how to calculate ieff for a partially composite steel beam? i can't find anything in s&j or online except for a reference to bs 5950-3). check out our whitepaper library. ieff = 0.75iequiv iequiv = provided as equation c-i3-3 on p16.1-309 of 13th edition (incorrectly noted as ieff). thank!!! that is quite a little gem that was tucked away in the commentary. willisv, i am not sure that's correct. what source did you use to decide that iequiv is the quantity computed using eq. c-i3-3? for what it's worth, my mentor back in grad school is one of the big-name aisc guys and has been teaching steel for 40 years and he uses eq. c-i3-3 in deflection calcs. of course, that's the way i've been doing it for years too, but it's just because i followed his lead. also, to further muddy the water, segui uses ieff=0.75itr in one of his example problems (page 580 of the 4th ed.). 271828- that note about iequiv is in the errata (i did look for that myself). i noticed ram also uses ieff=iequiv, not 0.75iequiv. also, my s&j text talks about using 0.33 to 0.5ec when determining itr to account for concrete creep and shrinkage. ok, perhaps that's correct. i think segui's method is clearly not correct because it totally leaves out the effect of more or fewer studs. even ilb in table 3-20 varies depending on sum(qn). |
所有的时间均为北京时间。 现在的时间是 04:37 AM. |