more windy componets cladding
more windy componets & cladding
wind loading on a large garage door (horizontal slider). given the following parameters: v = 90 mph i = 1.0 kd = .85 kz = .98 kzt = 1.44 asce 7-02 section 6.5.10: qz = (.00256)*kz*kzt*kd*v^2*i = (.00256)(.98)(1.44)(.85)(90^2)(1.0) = 24.87 psf now for the c & c design wind pressure for a low rise building (< 60') see asce 7-02 section 6.5.12.4: p = qh[gcp-gcpi] where gcpi = .55 gcp = 0.90 = -1.00 then p = 24.87*[0.90 -.55] = 8.71 psf or p = 24.87*[-1.0 – (-0.55)] = -11.19 psf this just doesn't see right to me for the wind load on a large garage door. the magnitude of the difference between positive and negative pressure seems about right, but i'm thinking the values should be about double what i get; what do you fellow designers think? where am i going wrong? you have the internal pressure coefficients reversed. when there is external pressure on the door, assume there is internal suction (0.9 + 0.55). likewise, with external suction, internal pressure (-1 - 0.55). daveatkins ok, so switching those around results in: p = 24.87*[0.90 -(-.55] = 36.06 psf or p = 24.87*[-1.0 – (0.55)] = -38.54 psf i fill better, although that's a pretty hefty wind load. it is about 18 psf more than in table 1609.6.2.1(2) for walls in zone 4. any thoughts on that? thanks dave! those are large c&c wind loads but it appears the cause of their magnitude is because you have a topo factor (kzt = 1.44) that has driven them up a bit. on large flexible doors, you will end up with catenary forces on the ends, meaning you will have to design the end connections for shear, but also axial forces. |