precasttilt up wall
precast/tilt up wall
for a precast/sitecast wall supporting a large dead load, what deflection would you limit to? i think h/180, but cannot find this for sure. thanks find a job or post a job opening l/180 sounds reasonable thanks, thats what i was thinking, but wanted to see what others thought. the maximum out of plane deflection, as per aci318-08, shall not exceed l/150. and, asce recommends using the following load combinations for the purpose. d+0.5l+0.7w d+0.5l+0.7e you can find these load combinations in appendix c of asce 7-05. hope this is helpful. strucguy very nice. thanks stucguy be sure to note that for slender wall design using aci318-08, section 14.8, service load deflection is to be calculated per equation 14-8, by iteration of delections. |