几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量

几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 (http://www.dimcax.com/hust/index.php)
-   产品功能分析 (http://www.dimcax.com/hust/forumdisplay.php?f=10)
-   -   shear breakout on appendix d (http://www.dimcax.com/hust/showthread.php?t=28579)

huangyhg 2009-09-15 09:30 PM

shear breakout on appendix d
 
shear breakout on appendix d
it seems to me when your bolt is far from the bottom edge, your shear breakout calculation is not making any sense (i.e. embed on the top of basement wall). i was expecting concrete pry-out controls most of it but it is not. is there something wrong with the formula? there are scenarios where i add more horizontal distance and my capacity goes down! that does not make any sense. what do you guys think? shall i neglect concrete shear break out? where is the fine line?
never, but never question engineer's judgement
find a job or post a job opening
funny you should mention that.
that is an issue i found several months ago when calculating the shear breakout capacity of a beam embedded into a panel.
this has been discussed before:
frv. which aci manual of concrete practice is it? we have 2005 and i cant find example 10.
never, but never question engineer's judgement