wind design
wind design
ok, lets say you have 40'x40'x60' tall building. on the top of building you have parapet that is 30'x20'x15' tall. so, when i design the components and cladding on the parapet, what is a? (10% of least horizontal dimension). is it the 40' or 20'? p.s. why is that all of the examples are always simple blocks when in reality it is not . never, but never question engineer's judgement check out our whitepaper library. the 10% least horizontal dimension, as i understand it, is with respect to the building. so this would apply to the 4 ft from the edge of the building. if the 30' parapet is centered on the building, then the 10% would not apply to the parapet. assuming your "parapet" is actually a screen wall (i gather that from your description, since a typical parapet would not be 15' tall), then i would use the 40' dimension. yes a screen wall, but i have to design it like a parapet. never, but never question engineer's judgement coenginner if you continue on in that section it also gives minimums, so any way 10% of 20 ft is 2 ft. 10% of 40 ft is 4 ft, and as stated in that section the minimum is 3ft. i would use 4ft for a (40ft length) and move on. jb |
所有的时间均为北京时间。 现在的时间是 01:47 AM. |