wood stud wall backing brick veneer deflection limitation
wood stud wall backing brick veneer deflection limitation
does anyone have a code reference for deflection limitation for a loadbearing wood stud wall backing brick veneer? thanks. check out our whitepaper library. what code are you designing to? bia suggests a deflection criteria of l/600. ibc states l/240 for brittle veneer. which ever criteria you use, the ibc and the fbc let you multiply the lateral load by 0.7 when calculating deflections. hope this helps. j i should clarify lateral load due to wind. |