主题: anchor bol
查看单个帖子
旧 2009-09-07, 11:50 AM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 anchor bol

anchor bolt
you use oversize holes for column base plate anchor bolt.
if anchor bolt is a307 or fm1554 what is it's capacity in shear?
p4-5 of asd manual does not have capacity for oversize holes for a307
also for oversize holes the connection needs to be slip critical right..
is it ok to use snug tight condition for oversize holes
for column base plate?
in this case, 4 bolts will resist shear right?
the only way you can get slip critical bolts in oversized base plate holes is to tighten against a nut under the plate. for significant force, you would then have to evaluate the bolts for bending.
there are better ways to provide for shear tranfer to the concrete. this topic has been discussed here at length. suggest you look for other threads which may give you assistance before this is rehashed.
if you have shear at the base of the column you should specify plate washers with standard holes between the column base plate and the nut. the plate washers are then field welded to the column base plate. look at table 14-2 of the 13th edition steel manual for recommended plate washer sizes.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)