超级版主
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
|
eccentric base plate pullout calc
eccentric base plate pullout calc.
i have an eccentric base plate located at the corner of a pier with uplift that has 5 anchor bolts. these bolts do not follow any pci 4 bolt pattern. does anyone know where to look for formulas or what they do in this situation? as always, many thanks for your ideas!
check out our whitepaper library.
if you have fem software available, perhaps you could model it on that.
aci 318-02 appendix d covers embedded anchors and has an adjustment factor for eccentric loading. i would try that. seems like the design would be standard procedure if you can get a good handle on the area of the concrete cone or truncated pyramid to use and the eccentricity of the load with respect to the bolt group c.g.
to calculate the ab stress in similar cases i have used:
fs = p/a +/- (mc)/i and keep the signs straight for the direction of load with i being the moment of inertia for the bolt group.
agree with twich, have designed similar as column reinforcement. s will vary with the ab locations, but still
p/a-+m/s is a good rule, apply stress reduction if applicable.
best, tincan.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
|